Quoted message said:It was mostly the bits about load for given cable widths,
Diameters. Many people wonder why electric cables are not marked
with a current carrying capacity. The reason is that the answer to
the question, "what current can this cable safely carry?" is, "it
depends."
Note that an accurate calculation will often sometimes allow one to
safely employ smaller cable sizes than the usual rules of thumb. A
rule of thumb is to use 1.5mm cable for short runs to immersion
heaters and 2.5mm for longer runs. I once used 1.0mm cable. After
doing all the calculations and planning a route that avoided other
cables it was clear that such a small cable could be safely used.
Had the run been longer it could not be used. As expected the cable
warmed up in use, but this was well within safe limits. More of a
problem are those who use the rules of thumb without checking them
with calculations. I have seen ring mains wired in 2.5mm cable in
locations where I suspect 4mm cable was necessary because of the
route taken by the cables through insulation. I suspect in many
cases thermal insulation is just installed, without considering
whether it will affect the electrical system.
The heat that can be allowed to be given off varies depending on the
construction of the cable and insulation, where it is mounted and
what external influences it suffers from (such as strong sunlight).
A suitable cable mounted out of reach on suitable mountings can be
allowed to run far hotter than one people can touch. It can also be
allowed to reach a far higher temperature if there is a fault.
Quoted message said:how many wires can
go in what kind of conduit etc for heat loss to be effective.
That is generally more of a consideration for large scale wiring.
However, in a house cables are often bunched when they approach the
consumer unit. It is wise to consider this bunching and take
appropriate precautions.
Quoted message said:Stuff that had
never really crossed my mind. (Not that running a cable to the garage
required such considerations..
You need to consider many things for such an installation. Does the
sun shine on the cable? Is the route above or below ground? What is
the design load? Voltage drop. Disconnection times. Protection of
the cable.
--
David Hansen, Edinburgh | PGP email preferred-key number F566DA0E
I will always explain revoked keys, unless the UK government
prevents me by using the RIP Act 2000.
----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! >100,000 Newsgroups
---= East/West-Coast Server Farms - Total Privacy via Encryption =---